    Converting kW/ton to COP or EER



    The efficiency of chillers depends on the energy consumed. Absorption chillers are rated in fuel consumption per ton cooling. Electric motor driven chillers are rated in kilowatts per ton cooling.
    KW/ton=12 / EERKW/ton=12 / (COP x 3.412)COP=EER / 3.412COP=12 / (KW/ton) / 3.412EER=12 / KW/tonEER=COP x 3.412
    If a chillers efficiency is rated at 1 KW/ton, the COP=3.5 and the EER=12
    Cooling Load in - kW/ton

    The term kW/ton is common used for large commercial and industrial air-conditioning, heat pump and refrigeration systems.
    The term is defined as the ratio of the rate of energy consumption in kW to the rate of heat removal in tons at the rated condition. The lower the kW/ton the more efficient the system.
    kW/ton = Pc / Er (1)
    where
    Pc = energy consumption (kW)
    Er = heat removed (ton)
    Coefficient of Performance - COP

    The Coefficient of Performance - COP - is the basic unit less parameter used to report the efficiency of refrigerant based systems.
    The Coefficient of Performance - COP - is the ratio between useful energy acquired and energy applied and can be expressed as:
    COP = Eu / Ea (2)
    where
    COP = coefficient of performance
    Eu = useful energy acquired (btu in imperial units)
    Ea = energy applied (btu in imperial units)
    COP can be used to define both cooling efficiency or heating efficiency as for a heat pump.
    • For cooling, COP is defined as the ratio of the rate of heat removal to the rate of energy input to the compressor.
    • For heating, COP is defined as the ratio of rate of heat delivered to the rate of energy input to the compressor.
    COP can be used to define the efficiency at a single standard or non-standard rated condition or a weighted average seasonal condition. The term may or may not include the energy consumption of auxiliary systems such as indoor or outdoor fans, chilled water pumps, or cooling tower systems. For purposes of comparison, the higher the COP the more efficient the system.
    COP can be treated as an efficiency where COP of 2.00 = 200% efficient For unitary heat pumps, ratings at two standard outdoor temperatures of 47oF and 17oF (8.3oC and -8.3oC) are typically used.
    Energy Efficiency Ratio - EER

    The Energy Efficiency Ratio - EER - is a term generally used to define the cooling efficiency of unitary air-conditioning and heat pump systems.
    The efficiency is determined at a single rated condition specified by the appropriate equipment standard and is defined as the ratio of net cooling capacity - or heat removed in Btu/h - to the total input rate of electric energy applied - in watt hour. The units of EER are Btu/w.h.
    EER = Ec / Pa (3)
    where
    EER = energy efficient ratio (Btu/W.h)
    Ec = net cooling capacity (Btu/h)
    Pa = applied energy (Watts)
    This efficiency term typically includes the energy requirement of auxiliary systems such as the indoor and outdoor fans and the higher the EER the more efficient is the system.

  2. [2]
    apo_mosa
    apo_mosa غير متواجد حالياً
    عضو فعال
    الصورة الرمزية apo_mosa


    تاريخ التسجيل: Sep 2006
    المشاركات: 109
    Thumbs Up
    Received: 3
    Given: 0
    مشكور أخي على إهتمامك

    0 Not allowed!



  3. [3]
    مهندس الشرقيه
    مهندس الشرقيه غير متواجد حالياً
    عضو فعال جداً


    تاريخ التسجيل: Jul 2006
    المشاركات: 151
    Thumbs Up
    Received: 6
    Given: 0
    ربنا يوفقك

    0 Not allowed!



  4. [4]
    amerhvac
    amerhvac غير متواجد حالياً
    عضو


    تاريخ التسجيل: Mar 2006
    المشاركات: 24
    Thumbs Up
    Received: 0
    Given: 0
    شكرا على التوضيح ...
    للمزيد
    معلومات هندسية عن COP ، EER
    معامل أداء دائرة التبريد Coefficient of Performance - COP
    نسبة كفاءة الطاقة Energy Efficiency Ratio - EER
    المصدر
    http://www.engineeringtoolbox.com/cop-eer-d_409.html

    0 Not allowed!



  
الكلمات الدلالية لهذا الموضوع

عرض سحابة الكلمة الدلالية

RSS RSS 2.0 XML MAP HTML